Join

Boards / Sizing and buying

Do mini splits use a lot of electricity? Members post their meter readings

Sizing and buyingOpen threadTech verified answer4 replieslast reply 3 days ago

Thread summary, kept up to date by the moderators

Do mini splits use a lot of electricity? No, not for what they do. A typical 12,000 BTU unit draws a few hundred watts while it is holding a room steady and somewhere around a thousand when it's working flat out, which is less than a hair dryer. Members who put a meter on their unit keep posting numbers lower than they expected, but the number depends heavily on the house, the weather and how the unit is used, so here's what moves it.

What the readings look like

From the meter threads on this board, a single 9k or 12k unit cooling one well-insulated room through a hot month lands somewhere around 100 to 250 kilowatt-hours. Multiply that by what you pay per kilowatt-hour and you have the monthly cost, so at 15 cents that's roughly $15 to $40.

Heating takes more because the colder it is outside, the harder a heat pump works for each unit of heat. A January month in a cold state can run two or three times a July month for the same room, though it's still well under what baseboard or space heaters would use to make the same heat. Your unit's nameplate and spec sheet list its rated and maximum input in watts, and that is the ceiling. Most hours of the year it runs far below it.

Why inverter units use so little

Older air conditioners have one speed. They run at full power until the room is cold, shut off and start again when it warms up, and every start is a surge. Nearly every mini split sold now is an inverter unit. The compressor slows down as the room approaches the setpoint and then idles along at a fraction of full power, matching the heat coming in through the walls. Long, slow running is where the efficiency comes from. It is also why the room feels more even.

What runs the bill up

  • A leaky or uninsulated room. A garage with a bare steel door can double the load of a finished room the same size.
  • A dirty filter or coil, which makes the unit run longer and harder for the same result.
  • An oversized unit that can't slow down enough and cycles on and off.
  • Turning it off and on all day. Recovering a hot room takes a long run at high power.
  • Very low heating setpoints outdoors, where every heat pump loses efficiency.

Sizing is the one you only get to choose once. The Sizing and buying board is where to post your room before you order.

How to measure your own

For a 115 volt unit that plugs in or sits on its own circuit, an inexpensive plug-in or inline energy meter gives you kilowatt-hours directly. For 230 volt units, members use a clamp-style energy monitor in the panel, or simply compare the same month's bill before and after.

Give it a full month before you judge. One hot afternoon tells you very little. If your numbers look high, post them with the room size and outdoor temperatures on the Troubleshooting board.

Quick answers

Is it cheaper to leave a mini split on all day?

Usually, yes, if you are home most days. Holding a temperature at low speed tends to use less than letting the room heat up and pulling it back down. If you are gone for days, set it back or turn it off.

Do mini splits use electricity when they are off?

A few watts for the electronics, and in cold weather some units run a small heater in the outdoor unit. It is small, but it's not zero.

Does a mini split use more power heating or cooling?

Heating, in most climates. The temperature gap between inside and outside is usually bigger in winter than in summer, so the unit works harder to move heat when it is cold out.

The thread: 4 replies

budget_brenda
Member

About to order a 12k for a 500 sq ft apartment over our barn. Power here is 16 cents a kWh. I keep reading these are cheap to run but nobody gives a number. What do people actually see?

Tech verified
Tomás
Load calculation and design, 7 years

For a reasonably insulated 500 sq ft space, cooling season is typically 100 to 250 kWh a month for a 12k, so $16 to $40 at your rate. Heating depends on your winters. Tell me your state and how the walls and ceiling are insulated and I can narrow it.

meter_mike
Member

I've had a plug-in meter on my 115 volt 12k for two years. 450 sq ft insulated shop in Tennessee. July: 142 kWh. January: 231 kWh. Spring and fall months are under 60.

Watching it live, it sits around 280 to 350 watts most of the afternoon and only goes over 900 for the first twenty minutes if I let the shop get hot.

Marcus
Electrician, 21 years

One wiring note since you are planning: the unit needs its own circuit sized to the nameplate. Low running watts does not change that. The breaker is sized for the maximum, not the average.

budget_brenda
Member

That's a lot less than the two space heaters I'm running now. Walls are R-13, ceiling is R-30, we are in Kentucky. Ordering it.

This is an open thread, so you're reading all of it. Join to reply or to ask your own.