Good result. Look at the flare face before you close it up next time. It should be smooth and even all the way round, with no ridge from the tool. If you see a ring, redo it.
12k unit with a 16 ft line set. I found soap bubbles on the 3/8 flare at the indoor side, so I cut it back and reflared twice, but it still weeps under nitrogen at 300 psi. I'm using the flaring tool that came in a kit, and I've tightened it about as hard as I can with two wrenches.
Three things, in the order I see them go wrong. First, deburr the inside of the cut with the tube pointing down so no chips fall in, and stop before you thin the wall. Second, put one drop of refrigerant oil on the back of the flare so the nut turns on the copper without twisting it.
Third, and this is probably your leak: "as hard as I can" is too hard. Over-tightening thins the flare and it cracks or cold-flows, so use a torque wrench and the number in your manual for 3/8.
I borrowed a torque wrench and I was way past spec. I made a new flare, added a drop of oil, torqued it properly and it has held 300 psi for an hour.