How long do I hold vacuum, and what micron number is good enough?

Install helpTech verified answer23 replieslast reply 31 min ago
porchlight
Member

Pump has been running 40 minutes on a 25 ft line set. The compound gauge on my manifold is pinned at the bottom. Can I open the valves?

Tech verified
Dale
Mini split installer, 14 years

The manifold gauge can't tell you. It reads the same at 5,000 microns as at 300, so you need a micron gauge placed at the unit and away from the pump.

Pull below 500, valve off the pump and watch. If it rises a bit and levels off under about 1,000, you're dry and tight. If it keeps climbing, you have a leak. If it climbs and stalls high, there's still moisture.

22 more replies in this thread, including the fixJoin to read the rest