Line set is 25 ft and I only need 12. Coil the extra or cut it?

Install helpOpen threadTech verified answer3 replieslast reply 3 hr ago
MaineMike
Member

The pre-charged line set that came with my unit is 25 ft, but the run from head to condenser is only about 12. Can I shorten it?

Tech verified
Priya
Refrigeration tech, 9 years

If it's a pre-charged line set with sealed quick-connect ends, don't cut it. The charge is already in there and you'd lose it if you opened it up.

Coil the extra behind the outdoor unit instead. Lay the coil flat, like a garden hose on the ground, not standing up like a wheel. A vertical coil makes traps where oil pools, so keep the bends wide and don't kink the insulation.

MaineMike
Member

Flat coil it is. Does the extra length hurt efficiency much?

Dale
Mini split installer, 14 years

Not enough to notice at 25 ft. Your manual lists a maximum length and the factory charge covers up to some point below that, so you're well inside both. Just insulate any bare spots and strap the coil so it can't vibrate against the wall.