Outdoor fan runs but the compressor never starts. No error code showing

Troubleshooting9 replieslast reply 2 hr ago
J_Okafor
Member

Two-year-old 9k unit in a bedroom. Indoor fan blows room-temperature air. Outside, the fan spins but I never hear the compressor. No code on the display.

Lena
HVAC service tech, 11 years

Start with the easy things first. Is it in cooling mode with the setpoint well below room temperature? If so, give it a full ten minutes because some units delay the compressor after power-up.

If it still never starts, tell me what voltage you're reading at the outdoor terminal block and whether the outdoor board has a status light that's blinking.